Ermon

Forum Replies Created

Viewing 9 posts - 1 through 9 (of 9 total)
  • Author
    Posts
  • #7445
    Ermon
    Participant

    Have fun my friend.

    #7439
    Ermon
    Participant

    Picture

    Attachments:
    You must be logged in to view attached files.
    #7438
    Ermon
    Participant

    I added the adjust downstream of the occupied and unoccupied strategies and sent the value to the controlling PIDs. This stopped the doubling effect.

    #7437
    Ermon
    Participant

    I run into the same problem. It looks like the stat adds the adjusted number to the setpoint Override output and adds it to the display. When I add the adjust to the strategy it in turn sends the value back to the stat thus making the value double. I am going to try feeding the Setpoint Override in downstream of the active setpoint. This is my first Fusion Stat.

    #7082
    Ermon
    Participant

    Thanks

    #7048
    Ermon
    Participant

    No more problems but not clear on how it got got changed.

    #6980
    Ermon
    Participant

    This happened again and I ran NbPro. I found that the point attribute out of service was true. I changed it to false and it started working. The output is a relay on a flx4. The controller is not connected to a network yet. I have another unit identical that works fine. Going to change out flex and down load.

    #4436
    Ermon
    Participant

    Jeremy I am with Ermon Controls Danville Ga.

    #4373
    Ermon
    Participant

    Jeremy who do you work for.